see now i'd have thought a 13A fuse should blow if it anything more than 13A is put through it. it's a bit silly really imo.. its not doing what it says on the tin.
shush
It will, eventually, but with an inverse time characteristic; i.e. the higher the overload the faster it will blow.
e.g... short circuit, a few thousand amps flow, fuse blows in a matter of milliseconds
constant but not too heavy overload (20-30A), fuse may carry this for several minutes before it blows
very slight overload (14A), fuse may well cope with this for several hours/days/weeks before failing.
The rating of a fuse is NOT the current at which it blows; it it the current that the fuse is designed to carry consistently without failing. You wouldn't want a 3kW heater (which draws nearly 13A constantly) to constantly blow the 13A fuse in it's plug.
Fuses are pretty crude and imprecise devices; they rely on the heating of a thin conductor to melt it. It's impossible to make a fuse that will blow instantaneously at exactly 13A. The idea is that a serious fault will pull enough current to blow the fuse pretty quickly. They're intended as protection against short circuit faults and severe overloading, NOT against relatively small overloads.
If you were trying to run 2 kettles on a 13A MCB (well, 16A really - 13A isn't a standard rating for an MCB) then the MCB would trip very quickly as they operate more predictably and with smaller tolerances than a fuse.
also depends on the rating of the kettles; at 240V, 13A gives a power of 3120W. 2500W@240V requires 10.4A; so your 2 kettles are actually pulling 20.8A. This isn't high enough for the fuse to blow straight away, it'll hang on for a while before the fuse element heats up to melting point. How long that takes is anyone's guess; depends on the design of the fuse itself and its manufacturing tolerances.